Manuals Sensor CEM v3.1 User Manual 8867.Sensor CEM User Manual RevA 2000.pdf 8865.Sensor CEM User Manual v1.3.0 1997.pdf 2117.Sensor CEM User Manual v2.0.4 1994.pdf 8461.Sensor CEM User Manual v2.1.4 1996.pdf 3175.Sensor CEM User Manual v2.1.4 1996.pdf 7206.Sensor CEM User Manual v3.0.0 1998.pdf 2117...
-
Problem: Dimmer modules slide out about 1/2" during transport of the rack. Modules must be re-seated before each use. Solution: Install (2) 7053A3087 Module Retainers per door (i.e. 2 per SP24, 4 per SP48). This will help to hold the modules in place.
-
What are Unique Dimmer Numbers? Sensor Unique Dimmer Numbers (UD#'s) are a new addressing scheme introduced with Sensor version 3.0 software. Unique dimmer numbers allow multi-rack systems to reference discreet, absolute dimmers beyond 512. In 2.x versions of CEM code, you merely entered a Starting...
-
On the first (primary) PCB of a Sensor SBS station, the jumpers should be set to 1 and 5. On the second PCB of a Sensor SBS station, the jumpers should be set to 2 and 6.
-
If Sensor racks are not mounted on a wall, there are keyholes on the rear of the rack which need to be covered. If these holes are left exposed, one could reach in and contact the bus bars. There is a kit to cover these holes. The kit contains (3) plates and (6) screws. The P/N for the kit is 7051K1001...
-
Question: What are the Fuse Changes for a Delta CEM? Answer: CEMD (120V Delta CEM) F2 changes from 1/8 Amp to 1/2 Amp. HCEMD (240V Delta CEM) F2 changes from a 1/8A. to 1/2 A. F3 changes from a 2A. to a 1A.
-
Sensor Backup Station (SBS) Pinout Pin Signal 1 12Vdc 2 GND 3 ETCLink Data - 4 ETCLink Data + This same pinout is also used for DAS stations.
-
Question: How Do I Wire and Use CEM Panic? Answer: CEM Panic is a contact closure which is wired to the CEM backplane in a Sensor rack. When the contact is closed, all dimmers which have been recorded into the Panic look are brought to full. Note that in multi-rack systems, the Panic switch is wired...
-
Problem: CEM displays Illegal Scale Error Message. Answer: Cause Can be the result of some corruption in the config, but does not impede system operation. Seems to be prevalent in large linked systems or CUDI systems Workaround / Fix There are many things that can make the message go away, but none of...
-
Question: How do I terminate ETCLink on a Sensor backup station? Answer: Insert jumpers on J5 A and B